Can the ITR040362041 take power from a 230V generator and deliver it to a 120 volt Multiplus?
Victron Energy ITR040362041 Isolation Transformer 3600W 115/230V 32/16A
The goal is to use the american multiplus to charge the battery bank from the european generator. The hertz shouldn't be a problem.
Status:
Open Mar 25, 2024 - 06:45 AM
1answer
Answer
Mar 25, 2024 - 06:45 AM
Yes you can use it like that. You just need to make sure you don't overload it. The limit is 16 amps @ 230 volts and so you should protect the input side with a 16 amp circuit breaker, then on the MultiPlus set the incoming current limit to 30 Amps